DaveSeattle
Well-Known Member
Hi all,
I am trying to replace a motorized ball valve with a solenoid on my HLT, but the solenoid doesn't open properly: it only lets a tiny dribble of water through. Does anyone know what could cause this?
I verified:
Here is the interesting bit: the solenoid does open fully if I give it a good long suck (insert jokes here), as if it weren't getting enough water pressure to open the diaphragm. And I have others of these units on city water pressure lines that open properly. But they're sold as gravity-fed and rated for 0-0.8Pa.
Any ideas what the issue could be here?
David
I am trying to replace a motorized ball valve with a solenoid on my HLT, but the solenoid doesn't open properly: it only lets a tiny dribble of water through. Does anyone know what could cause this?
I verified:
- That the marked arrow points in the direction of flow
- That the solenoid expects and is getting 12v DC
- That the water flows at the expected rate from the HLT without the solenoid in place
- That it's not just a defective part, by trying multiple different units (of the same type).
Here is the interesting bit: the solenoid does open fully if I give it a good long suck (insert jokes here), as if it weren't getting enough water pressure to open the diaphragm. And I have others of these units on city water pressure lines that open properly. But they're sold as gravity-fed and rated for 0-0.8Pa.
Any ideas what the issue could be here?
David