"but 400 CFM is okay for electric but definitely not okay for gas."
400 CFM would be OK for gas, as long as a 300K BTU flame thrower wasn't fired up.
Rule of thumb for commercial hoods with commercial gas burners. 50 CFM per sq/ft of hood opening, 100K BTU, when the burners and hood are against a wall. Static pressure is not taken into account.
100 CFM per sq/ft, 100K BTU, when the burners and hood are in the open. (island) Static pressure is not taken into account.
Fresh air requirements for combustion, 1 square inch per 1K BTU input.
When there are gas fired, oil fired or wood burning, atmpspheric, appliances in the brewery, (chimney vented wood or gas fireplace, chimney vented boiler, furnace, water heater) will be affected by the hood's exhaust. In which case, make up air will need to be supplied, to offset negative pressure. Sealed burner, direct vent appliances are not affected.