I need to ask a question that's very off-topic for HBT but this seemed like a good place to catch the Electricians in the house. I have a question about my home service and would appreciate it if one of you would PM me and allow me to ask you a question or two.

Um .... BEER! :)
 
There are a lot of electrician here. I say just ask. Off Topic? If its a DIY I think you are in the correct space.

Feel free to send me a PM if you would rather.

Cheers
Jay
 
True!

Well, I'll share here then: I need to replace the line from the (is it called a mast?) to the breaker box, and the breaker box as well actually. I think I need split nuts, cambric and rubber tape, up for the mast connection, and that's how it's connected? Looking for the right words to use.

I'm in a rural area where there's no inspections, and I'm not afraid of 220 (three phase or an inverter and I might shake a bit.) Just need to words to look up what I need.
 
Last edited:
Check with your power company about who can make the connections for the "mast". Back in the day they would let us do it, but most states and power companies now require that they make the connections. A quick call may help you out.
 
Check with your power company about who can make the connections for the "mast". Back in the day they would let us do it, but most states and power companies now require that they make the connections. A quick call may help you out.
Unfortunately this is private service - from the house to the barn.
 
So you're not referring to the connection to the "street"?
If you're running a line from your load center to a shed or barn I'd think you can do pretty much anything you want that can carry the amperage...particularly if you run the wire underground in a PVC conduit...

Cheers!
 
True!

Well, I'll share here then: I need to replace the line from the (is it called a mast?) to the breaker box, and the breaker box as well actually. I think I need split nuts, cambric and rubber tape, up for the mast connection, and that's how it's connected? Looking for the right words to use.

I'm in a rural area where there's no inspections, and I'm not afraid of 220 (three phase or an inverter and I might shake a bit.) Just need to words to look up what I need.
I get nervous when I see wire strung through the air and held with split bolts. If you aren't comfortable with the work, I'd highly recommend calling an electrician out. They aren't cheap but electricity can potentially cause death and mayhem if it's done incorrectly.
 
Service entrance cap like this one if you're just strapping the service entrance cable to the wall. This weather seals the opening of the outer jacket of the cable so water doesn't pour down the jacket. They are sold based on the cable sizing.

1644387623502.png

The other option is to put it in a conduit and they make a version of the entrance cap that mounts on the top of a conduit.

To support the cable on each end of an aerial you need cable grips but for a heavier cable and longer run, you can buy cables with a built in steal support cable that gets connected to eyebolts on each end. I suppose you can rig a support cable parallel yourself and secure it to the cable.

The splice between the service entrance cable and the aerial can be done with weatherproof splice lugs like this:
1644388067334.png


However, if you're running the cable down a conduit with conduit mounted drip cap, you don't need to splice necessarily when replacing both the aerial and vertical drop.
 
I appreciate the warnings. I'm (obviously) not an expert, but messing with AC voltage is not something I've never done. I've just never done this type of connection.

A little more of a description is in order: There is an existing aerial run to the barn. "Up there" is a connection from the other load panel at the house to the barn and then also to a back building. So it's a 1 into 2 split. From where I stand it looks like it's just a ball of electrical tape, but I assume (maybe dangerously) that it's something more than that. i want to know what I am getting into before I climb the ladder, because stores are not close around here. That's why I am looking for the right words for the parts and pieces.

I need to do the work because the load panel in the barn is decrepit. I need to add a 50A circuit to it for my camper. The line coming in from the mast is (guessing) #2 aluminum. I intend to replace the line from the mast to the panel and then of course the panel itself. It's maybe a 10' run. The replacement is because I'm thinking (maybe incorrectly) that "aluminum is bad" but maybe it's okay in the main coming in? I do see someone coated the terminals, so that at least was done correctly.

If the line from the other pole where this service starts is aluminum, I believe I need a different connector than a split bolt. Possibly a polaris connector? That showed up in some searches. I believe at least one of the three being connected now are copper because it's only a few years old. I'm going to go check the other end to be sure.

Then some time in my past I remember some dude smarter than me that y9u should use cambric tape first over a terminal like that so you can cut it off again if needed. So I was intendeding to use that, rubber tape and then follow it up by good old Super 88.

So that's the project. I need to know the right stuff to look for so I can get my shopping done before I start. There's no running to the corner hardware after I start. :)
 
Do a Google (or the search engine of your choice) search for "insulated multi-tap connector" and you'll find exactly what you need for connecting the wires. Available in many wire sizes, with different numbers of openings, and already insulated so no taping required. They are AL/CU rated so you can connect AL to AL, CU to CU, or Al to CU. Insert the cleaned (with a stainless steel wire brush) stripped wire end, tighten the set screw, and you're done. For single phase you'll need 3 of them, one for the neutral and one for each hot leg. They're what we used at the power company for tapping multiple overhead services to the end of a single secondary cable. For the mast use either galvanized or Schedule 80 PVC attached to the building with mast straps and install a weatherhead on the top, the wires from the panel exit the weatherhead towards the ground so water will not run into the mast. Make sure to leave a drip loop in the wires. Install a "service entrance wedge clamp" on the neutral conductor to attach the end of the wire to the building using a secure attachment point like a heavy duty eye bolt. If you search for "FPL ESS" (Florida Power & Light Electric Service Standards) and download the document, there's diagrams of service connections in section IV (I was one of the author/editor/revisors of the book). P.S. - Aluminum is not bad, it's what the power company uses in 99.99% of all the installations, you just need to clean the wire properly, use oxidation inhibiting grease (already inside the multi-tap when you buy them), and torque the connections properly.
 
Thank you! Exactly what I needed.

So if Al is not inherently "bad" is there any reason to change out the drop from the mast, or can I just re-use that for the new load center? The sheathing on the cable itself is fiber-wrapped, not sure if that makes a difference in the answer.
 
If it's fiber wrapped then it's pretty darned old, I'd just go ahead and replace it to avoid any future issues with the insulation coming off. #2 AL triplexed HDPE insulated bare neutral service cable (feeding the mast) is less than $2.00 per foot. Inside the mast (from weatherhead to panel) use 3 insulated single #2 AL (or larger) conductors, the #2 AL 90C rated conductors are good for 100 amps. If it was a permitted installation built per the NEC, you'd need larger wire since you cannot load them to 100% of rating under the code (since the power company is exempt from the NEC, we loaded everything at 100% for our calculations and could therefore use smaller wire sizes - that's why you'll see a #1/0 AL triplex service cable feeding a #4/0 CU conductor inside a mast. The splices between the service cable and the mast conductors is the demarcation point between power company (#1/0 AL) and house wiring (#4/0 CU)).
 
Yikes! Yeah this is all above-ground, no worries there. Sounds like Al is a lot cheaper than Cu too. I've never gone and purchased this by the foot - I may need to find a real electrical supply place to get some.
 
I think I'm going to take some pics and post them here after the call I am on gets done. I'm betting there's a better way to skin this cat.
 
Okay here's the whole job. My "need" is to replace/update the load center inside the barn because every time I take the face plate off the breakers pop out. I also need to add a 50A circuit for my travel trailer and despite there being amperage availability technically, and space physically, I get a bad feeling working in that box.

So with that in mind, maybe some of you smart people can suggest a good way to go. The project consists of:
  • Quonset Hut (or "barn") with the mast
  • Out-building with the new service split off the mast and running underground from the Quonset
Here's the mast up top (all of these should be clickable to get the larger versions). There's a 200A breaker feeding this overhead line:
Mast.jpg

You can see the old fabric-covered cable running down/right and the newer one with the weather head underneath. The older one serves the Quonset and is the one I am concerned about. The newer one serves another out-building via an underground from the Quonset.

Here's the inside of the barn on the other side of the mast:
Inside Feed.jpg

The fabric-covered one is low-left and the new one is middle-right.

Here is the load center with the fabric-covered service coming in the top, and you can also see the new HDPE (I think) covered service running down the left of that.
Load Center Outside.jpg

And that new service passes through the wall below the load center above and ties to the underground service in this box:
Barn Junction - Inside.jpg

If that new service were something larger than #2, I could cut it inside and split it in a trough above a new load center. I am fairly certain I cannot run #2 @ 200A. So I am left with (I think) running a new #2 from the junction up top down into a new load center (with a new weather head.)

Does this seem like the right way to go?
 
I would simply install a new weatherhead of the same type right next to the existing "new" one and run the same kind of "new" cable from that weatherhead to the new service panel. Since the breaker protecting this installation is 200 amp you'll need to size the new wire to handle 200 amps. Here's a link to a cable ampacity chart: Allowable Ampacities of Insulated Aluminum or CopperClad Aluminum Conductors On American Wire Group - Use the insulated multitaps I mentioned earlier to tap both of the weatherheads to the existing OH service cable, no need to do anything with that service cable, it's in fine condition. Rip out the old cable and patch the hole. Easy-peasy.
 
I would simply install a new weatherhead of the same type right next to the existing "new" one and run the same kind of "new" cable from that weatherhead to the new service panel.
Thank you @esdill. The new feed is #2 Al according to the sheathing. I think. Here's what the printing says:
Code:
E194993 3 CORS 2 AWG AA-8000 AL 1 COR 4 AWG AA-8000 AL TYPE SE STYLE R-XHHW-2 CDRS 600 V XLPE (UL) 2005
I think that's polyethylene sheathing rated for wet conditions with 3 #2 Al conductors and a #4 Al ground? There's no ground in the Quonset that I can see, unless it's bonded somewhere up top at the mast.

Since the breaker protecting this installation is 200 amp you'll need to size the new wire to handle 200 amps.
It looks like a 4-pole 200A breaker. This is in a box underneath (inside) the meter. Is it possible that the electrical service is split there to the house and to the Quonset, 200A for each? I'll open that box and take a pic.

Oh the joys of buying an old farm!

Use the insulated multitaps I mentioned earlier to tap both of the weatherheads to the existing OH service cable
Like this one?
1644436567534.png
That's what I meant by "Polaris" - apparently they are a manufacturer?

Now I definitely owe ya a beer!
 
Yep - 200A and what looks like 4 poles but two are on the same bar?
Main - Inside.jpg

Main Breaker.jpg

I don't know if that's 4 x 100A with two in parallel or what?

Anyway, that service looks like copper but I don't see the wire size on it. I'd ASSume it was 4/0 since it's recent, but who knows. I think this part is owned by the Rural Electric folks - worth a call to them anyway.

The problem is, that's the ONLY breakers outside before this splits to the barn, the Quonset, the back-building and the house. I'd think it would be smarter to get a new 50A GE breaker and run the service from there to my Camping Trailer?
 
Was that line rated for direct burial ?

Heck if I know. but assume so - power company put it in 35 yrs ago. They tried an underground patch, but that didn't last long. Came back later with some serious equipment and tunneled a whole new line from the transformer to my house, in a semicircle around my cul-de-sac. Not an easy job. Took several days. New line looked a lot like the old one, definitely not in conduit.
 
Yep - 200A and what looks like 4 poles but two are on the same bar?
View attachment 758923
View attachment 758924
I don't know if that's 4 x 100A with two in parallel or what?

Anyway, that service looks like copper but I don't see the wire size on it. I'd ASSume it was 4/0 since it's recent, but who knows. I think this part is owned by the Rural Electric folks - worth a call to them anyway.

The problem is, that's the ONLY breakers outside before this splits to the barn, the Quonset, the back-building and the house. I'd think it would be smarter to get a new 50A GE breaker and run the service from there to my Camping Trailer?
Yes, those are paralleled 100 amp breakers connected together with a tie bar to make 2 - 200 amp legs ... a cheaper way to do it for the manufacturer, but no longer allowed under the NEC. And yes, you could install a 50 amp breaker in there and run the service to the trailer directly from there, assuming it's close enough to where you want the trailer to be set up.
 
Thank you @esdill. The new feed is #2 Al according to the sheathing. I think. Here's what the printing says:
Code:
E194993 3 CORS 2 AWG AA-8000 AL 1 COR 4 AWG AA-8000 AL TYPE SE STYLE R-XHHW-2 CDRS 600 V XLPE (UL) 2005
I think that's polyethylene sheathing rated for wet conditions with 3 #2 Al conductors and a #4 Al ground? There's no ground in the Quonset that I can see, unless it's bonded somewhere up top at the mast.


It looks like a 4-pole 200A breaker. This is in a box underneath (inside) the meter. Is it possible that the electrical service is split there to the house and to the Quonset, 200A for each? I'll open that box and take a pic.

Oh the joys of buying an old farm!


Like this one?
View attachment 758915
That's what I meant by "Polaris" - apparently they are a manufacturer?

Now I definitely owe ya a beer!
The wire code you have transcribed is 3 - #2 AL hot legs and 1 - #4 AL neutral ... no idea why they used that for single phase since you only need 2 hot legs and a neutral ... and it's undersized based on the upstream protective device being a 200 amp breaker. For 200 amps you'll need 2 - 4/0 AL hot legs and a 2/0 AL neutral to meet code.
1644448602791.png

I responded to the other post with the picture regarding the 4 breakers, they're 4-100 amp breakers tied together with a bar to give 2 - 200 amp legs. And yes, the multitap shown would be perfect, Polaris is the manufacturer of that one, but there's many other manufacturers as well and any manufacturer's similar device will do the job ... whatever you can find at the supply depot.
 
@bracconiere It looks looks @esdill has it well under control. Solid info being given already. No sense adding when none is needed. All I have is just make sure the connections are tight and then check again. Al will "flow" a bit in my experience after initial tightening. Also "Noalox" (or equiv.) is your friend.
May your electrons flow freely,
Cheers, :mug:
Joel B.
 
Yeah, the 2 AWG cable with the 200A breaker is no bueno - I get that. Looking at the service it's like that from the main breaker in. All three legs are simply split and not protected individually. I'd have to do some work at the first pole to make it all "right."

I'm re-thinking my effort. I have about a 50' run from the pole to where the travel trailer is. I may take a 50A off that main panel; to a disconnect by the trailer and know at least that much is right. I know I'll have to go back and re-work the rest but it's been like this for at least 20 years so I can probably wait a couple more.

I'll price out doing both though and figure out which way is best (for now.)

I appreciate all the help, folks.
 
fwiw, we have 200A service relying on 4/0 aluminum in the ground to a concrete vault shared with a neighbor. There's no conduit, just buried wire. The whole development was put in the mid-70s that way so while all utilities are buried they weren't done with much mind towards lifespans. Phone and cable were the same though we switched to buried fiber many years ago.

Many of the almost 200 homes started with 100A load centers and over the years when folks upgraded AC systems and added rooms and whatever and wanted to go to 200A service, the cable size was to code, but by then lots of them had degraded to where the homeowners had to dig up and replace them.

The neighbor I don't share a vault with had to have their feed replaced and their home has a ~400' set back plus another 100' of run parallel to the street to get to their lot. That was some expensive trenching right there. Before he got the wire replaced I remember watching his house blinking when he was messing around in his work shop - a good current thump would darned near black him out and I'm sure was causing lots of clocks to reset :)

We only have a 100' set back and the vault is on the property line, so it wouldn't be nearly as bad, but still, it's a liability that our feed could eventually go bad...

Cheers!
 
There is an instruction book for all of this. It is called the National Electric Code. If you are not comfortable reading that and understanding the requirements for the job you want to do then it would be wise to call an electrician that can.

I realize that sounds a little snarky but poor electrical work can have pretty severe consequences. The metal quonset hut might not burn but someone could get hurt. I see crazy stuff all the time that well meaning DIY folks did. People ask me “why would they do that?”. My answer is: because there was nobody there to stop them.
 
There is an instruction book for all of this. It is called the National Electric Code. If you are not comfortable reading that and understanding the requirements for the job you want to do then it would be wise to call an electrician that can.

I realize that sounds a little snarky but poor electrical work can have pretty severe consequences. The metal quonset hut might not burn but someone could get hurt. I see crazy stuff all the time that well meaning DIY folks did. People ask me “why would they do that?”. My answer is: because there was nobody there to stop them.
I worked for a company that had a metal hut building with sliding doors that hit a stop in the ground when closed. A certified electrician wired the hut. While closing the doors I damn near got electrocuted when they hit the stop in the ground. Current went through both arms as one door grounded first. I told the owner to get the GD jackleg back here now. Owner almost didn't believe it. I told him you come here and touch these doors then. Jackleg electrician failed to bond the panels among other things. Everyone around here thinks this dumb@ss is the best around here. Sad. At least when you hire a professional, you get insurance or can sue for damages when someone dies or something burns. I'm not knocking this diy here. I wish I still lived in Missouri. If I did, I would drive to Kansas city to help LBussy. I have buried and stung a lot of wire in my day.
 
For some reason, I can't quote anything from this thread .... weird.

I realized I never changed my location so I did that. For those of you who have known me for a while - I've moved. We've literally "bought the farm" down in rural Kansas.

The last person to touch this (seems like only a few years ago) added some outlets to this load box. He was a licensed electrician who should lose his license. So, hiring an electrician, other than him having a taller ladder and the right tools, hardly seems like the safe bet. Even if I do hire an electrician it looks like I need to learn about what's wrong with this setup. That allows me to gauge his approach and be an informed consumer.

Believe me, I appreciate the cautionary tales. In my path to get where I am, I did a stint installing building controls. At that time (no idea how it is now) there were no unions for that part of commercial construction, so we were left to learn things the hard way in some cases. We did some plumbing, some electrical, and some programming depending on the day. I had my favorite screwdriver go off like a flashbulb when I was working on a VFD. So, yeah, I get it. I don't want to die. :) I am not going to tell you I know as much as a good electrician. I am going to tell you once I know what is supposed to be done, I can do it safely.

I'm also aware of the NEC. That's why I was looking for "the words" so I would know what to look up. Reading the NEC is not really as engaging as Steven King, so having the right terms to go searching for will help me find what I need. I also appreciate the qualified advice I've received here. A one-liner from an experienced craftsman is worth its weight in gold. Just ask @day_trippr: I learned the hard way to listen to him. When he says "Vaya con Dios" I know I am bout to screw something up. :)

I think my biggest problem in this project will be that I can fix one thing but the next thing up the line will be wrong. I've had these sorts of projects before. It seems like I'm going to have to survey the entire electrical system here and see what I can isolate before I can renovate it. Yay, rural living! It's looking like a trencher for the tractor will be a good investment (yes, that's a joke.)
 
If you are looking to save money, you can do the heavy lifting by pulling cables into place, mount hardware as required, etc. Hire an electrician to make the final connections verify everything is up to code.
 
If you are looking to save money, you can do the heavy lifting by pulling cables into place, mount hardware as required, etc. Hire an electrician to make the final connections verify everything is up to code.
Aha, I can quote again! :)

Saving money is always a consideration, making sure it's done correctly is another. If I go to the trouble to do all the heavy lifting, that would mean I have the tools needed; which I don't right now. I'm talking things like a ladder good enough to get to that mast, cable cutters, etc. If I had those things and got all that work done, there's nothing about the connection that worries me.

That would be like designing a beer recipe, buying all the ingredients, and then letting someone else make it. The hard part is the planning. :) (see how I got back on beer?)
 
For some reason, I can't quote anything from this thread .... weird.

I realized I never changed my location so I did that. For those of you who have known me for a while - I've moved. We've literally "bought the farm" down in rural Kansas.

The last person to touch this (seems like only a few years ago) added some outlets to this load box. He was a licensed electrician who should lose his license. So, hiring an electrician, other than him having a taller ladder and the right tools, hardly seems like the safe bet. Even if I do hire an electrician it looks like I need to learn about what's wrong with this setup. That allows me to gauge his approach and be an informed consumer.

Believe me, I appreciate the cautionary tales. In my path to get where I am, I did a stint installing building controls. At that time (no idea how it is now) there were no unions for that part of commercial construction, so we were left to learn things the hard way in some cases. We did some plumbing, some electrical, and some programming depending on the day. I had my favorite screwdriver go off like a flashbulb when I was working on a VFD. So, yeah, I get it. I don't want to die. :) I am not going to tell you I know as much as a good electrician. I am going to tell you once I know what is supposed to be done, I can do it safely.

I'm also aware of the NEC. That's why I was looking for "the words" so I would know what to look up. Reading the NEC is not really as engaging as Steven King, so having the right terms to go searching for will help me find what I need. I also appreciate the qualified advice I've received here. A one-liner from an experienced craftsman is worth its weight in gold. Just ask @day_trippr: I learned the hard way to listen to him. When he says "Vaya con Dios" I know I am bout to screw something up. :)

I think my biggest problem in this project will be that I can fix one thing but the next thing up the line will be wrong. I've had these sorts of projects before. It seems like I'm going to have to survey the entire electrical system here and see what I can isolate before I can renovate it. Yay, rural living! It's looking like a trencher for the tractor will be a good investment (yes, that's a joke.)
Have you looked into renting a small trencher ? I once saved a guy a bunch of $ and aggravation by running a big line around a building instead of moving stuff inside the building and using a lift to hang conduit up high inside. Maybe borrow or rent the tractor attachment ?
 
Not looked yet - just moved down here on the 31st so I'm still finding all the things I need to do. When I was in KC I had "people" I could reach out to - I don't have that here yet. Working on it though.
 
Reading the NEC is not really as engaging as Steven King
Well one of the more exciting parts of the NEC is grounding and bonding, very suspenseful and least understood. Seriously, if everything is grounded and bonded properly it goes a long way to preventing injury. That and ground fault protection in appropriate places (like a metal barn). One of the most confusing parts of the code is getting the equipment grounding system, grounding electrode system and bonding installation done properly for a downstream panel (subpanel) in a building that is a separate building and/or remote location from the main service panel; I believe it is referred to as a remote subpanel. You can't do it right without bringing 4 wires from the main panel. The safety concerns that require four wires have a lot to do with lightning strikes and other sources of stray current in the soil. I hear you have some lightning in Kansas.

Any new work that is done should conform with current standards. That doesn't mean you have to bring every existing thing you connect to up to code but the new installation should be compliant. So just copying what is there with new materials may not be a good idea. Many people have this mistaken concept of "grand fathered"; they think that if it was done that way originally it is OK to do it again or replace it the same as the old. Anything newly installed as an additional component or replacement component should conform with current standards.

If you want to search the NEC, some words or subjects you might need are: Service mast, service entrance, service drop, overhead conductors, weather head, conductor size, equipment grounding system, grounding electrode system, downstream panel, conduit fill (capacity). Being a long way from the main panel you should also look into conductor sizing as relates to conductor sizing.

A good internet source of information on electric code and its application is Mike Holt's Forum. They are not always so polite about conversing with folks that aren't electricians but searching the forums can yield a lot of valuable information.

If you have a farm you are going to want a tractor, right?
 
Last edited:
Well one of the more exciting parts of the NEC is grounding and bonding, very suspenseful
I'll be sure to print that out so I can read it while on the toilet. ;)

That and ground fault protection in appropriate places (like a metal barn).
Not a GFI to be seen plugging things in while standing on bare ground. :)

One of the most confusing parts of the code is getting the equipment grounding system, grounding electrode system and bonding installation done properly for a downstream panel (subpanel) in a building that is in a separate building and location than the main service panel; I believe it is referred to as a remote subpanel. You can't do it right without bringing 4 wires from the main panel.
Yeah, there are four, and I assume that was not because that was the only thing he had on the truck. I'll have a special search for that section to understand "why". I also see a lightning rod pretty darned close to that mast so I'll probably take a climb up there when I get away from the computer and see where that's grounded.

I hear you have some lightning in Kansas.
Every once in a blue moon!

Many people have this mistaken concept of "grand fathered"
Heh, it works no better for electrical codes than for anything else. I learned that the hard way some years back. I used to have my GC license and we did some work and learned the hard way about touching things that are not up to current code. Then there was a very similar issue with a gas line. We changed the service hose, then the line leaked, then we ended up working it all the way back to the meter before we got rid of leaks and could pass inspection.

If you want to search the NEC, some words or subjects you might need are:
Thank you, seriously, that helps a lot.

A good internet source of information on electric code and its application is Mike Holt's Forum.
And again, thank you. I search WAY more forums than I speak on so I am familiar with the concept of keeping my mouth shut while adults are talking. I learn a lot that way.

If you have a farm you are going to want a tractor, right?
I have one! Some Alice Chalmers that's older than me I think. One of the things "on the list" is to find parts for a turnbuckle that my father-in-law has been nursing along for a very long time.
 
I'll have a special search for that section to understand "why".
Unfortunately the code books are very poor for understanding "why". They are mostly prescriptive, not descriptive. This leads to some people, myself included, saying "That does not make any sense to me. I'm doing it my way or the old way". I did learn from a friend that served on a panel that worked on vetting new additions to the NEC that they don't add stuff just to prevent things that they imagine could happen. There have to be a certain number of documented cases that justify making a change or adding something new.
 
Unfortunately the code books are very poor for understanding "why". They are mostly prescriptive, not descriptive. This leads to some people, myself included, saying "That does not make any sense to me. I'm doing it my way or the old way". I did learn from a friend that served on a panel that worked on vetting new additions to the NEC that they don't add stuff just to prevent things that they imagine could happen. There have to be a certain number of documented cases that justify making a change or adding something new.
Yeah, that's frustrating. Maybe one of our resident EE's (I only know of one actually) could help with that. I'm stuck on a horrible call, digging trenches seems more attractive than this. Hopefully, I can do some studying here in a little while.
 
.... for a downstream panel (subpanel) in a building that is a separate building and/or remote location from the main service panel; I believe it is referred to as a remote subpanel. You can't do it right without bringing 4 wires from the main panel.....
This happens a lot. Some people don't want to pay for that 4th wire. GFCI breakers are useless with a 3 wire run. Some new sub panels do not come with a separate bus for ground and neutral so guys will put them both on the same bus and that will not work. Square D sells them separately for a couple of bucks. Manufacturers save a few dollars when making them and then they make a few more $ selling you the bar (bus). Sad. It should be standard. I have gone behind certified electricians that have left neutral or ground wires disconnected in 240v applications to keep GFCI breakers from tripping. There are electrical supply houses that refuse to take returns on GFCI breakers because so many get returned as defective that are NOT defective. All because a home owner or jackleg electrician did not know to install that $2.00 strip of metal, ha.
 