He hasn't shown you a picture of his box or even of the components in his box. For a magnetic/thermal breaker it doesn't matter which is input and which is output unless the panel in which the breaker is installed has wire lugs on one side and some sort of other terminals to mate with bus bars, for example, on the other.Excellent, just as I pictured in my head.
In my line of work, LINE almost without exception comes into the top of the breaker and LOAD exits the bottom.
I thought that was interesting too. Going to make for some interesting trouble shooting sessions.Interesting that a ground fault will open the bad circuit and five of it's friends on that phase.
He hasn't shown us connections for any three phase appliances. Just single phase branch circuits distributed across three phases. In all the stuff I've seen where a three phase load was protected by a GFCI/ELCB (or whatever you want to call it) the three phase conductors and the neutral all went through the doughnut in the breaker. Any current from any phase that did not return through one of the other phases or the neutral would trip the breaker disconnecting all three phases. Similarly, any magnetic or thermal overload on a single phase would trip the breaker and interrupt all 3.Podz, what condition exists when just one of the ground fault protectors trip on a 3-phase appliance? (I'm assuming the remaining two hold)
Does the main neutral bar get bonded to earth?
He hasn't shown you a picture of his box or even of the components in his box. For a magnetic/thermal breaker it doesn't matter which is input and which is output unless the panel in which the breaker is installed has wire lugs on one side and some sort of other terminals to mate with bus bars, for example, on the other.
Does the main neutral bar get bonded to earth?
As you are running separate neutral and protective conductors inside the building that would make it a TN-C-S. The grounding electrode puzzles me though. I'd be tempted to call that T(T/N)-C-S but there is, AFAIK, no such thing in IEC parlance. The NEC system is described as TN-C-S but also has the grounding electrode requirement at the service entrance.Yes, I have a TN-C system with PEN coming from the utility.
Yes, I have a TN-C system with PEN coming from the utility.
As you are running separate neutral and protective conductors inside the building that would make it a TN-C-S. The grounding electrode puzzles me though. I'd be tempted to call that T(T/N)-C-S but there is, AFAIK, no such thing in IEC parlance. The NEC system is described as TN-C-S but also has the grounding electrode requirement at the service entrance.
Anyway, it is most interesting to those of use completely parochialised by the NEC to get some exposure to how things are done in the rest of the world.
This old house doesn't have an equipotential bar, though I should install one and bury some copper in the yard. Connected to it should be the main breaker panel, rebar in the house, pipes, the metal roof, TV antenna, and ADSL connection.
Anyway, I've got neutral bonded to ground inside of the main panel and isolated inside the sub panels.
Still got four circuits waiting to migrate to the new panel. Those are a real pain because they trail through multiple rooms.
There really is no need to do that unless you have special requirements of some sort (swimming pool, milking parlour...) and even in those cases the best approach is an equipotential surface around the pool etc. rather than lower impedance to earth. In the US the requirement is that the impedance be 25 Ω or less. A single rod is usually sufficient but if you have uncooperative soil a second one may be required.This old house doesn't have an equipotential bar, though I should install one and bury some copper in the yard.
The problem you get into there is that a strike at one 'end' of the distributed ground injects HUGE current into the ground in its vicinity resulting in very large, very steep gradients. These induce very large currents in the grounding system some of which, on their way to the true earth potential at the transformer, may magnetically couple to the phases and damage electronic equipment. So that relates back to the question as to whether your utility uses a multiply grounded neutral (or a neutral at all). These are important in Canada (though they are used in the US as well) because of the large potential gradients induced by solar events. Even with MGN a CME in March 1989 wiped out Quebec's power grid. Shallow bedrock was cited as contributing to the problem. I'd guess it would be the same there.80cm is the min depth, but of course impedance testing is required before taking into use. the primary intention of the circular loop is remote lightning strike protection, i.e current traveling across the ground, which happens during the time when the ground isn't frozen.
We also have a very shallow bedrock across most of the nordic regions... rock is exposed in many places, even in my yard.
Driving a ground rod would require some heavy drilling and probably be pointless in the end.
What is the grounding system impedance requirement there?
Mittauksen suojajohtimen hyväksyttävä mittausarvo on 0,13 ohmia.
No problem. Just curious. Please don't worry about it any further.Sorry for being short, but the hand...
So, between 0.1 and 3 ohms.Mittauksen suojajohtimen hyväksyttävä mittausarvo on 0,13 ohmia.
ajdelange said:That actually refers to the protective conductor (no, I don't know any Finnish - the only word I know in the whole Finno-Ugric system is 'Sor', the Hungarian word for beer). I meant the requirement for the impedance between the grounding rod terminal and the earth. I (probably obviously) got the translation for the quote above from Google Translate and looked over the rest of the page. The translation isn't great but I did see reference to testing with inductive type meters but no acceptable value.
Nice thread post. Quite interesting to read since I'm from Sweden and most of the threads here are related to American standards.
Let me know what element you purchase and your experience with it. I'm on the same route as you are.
Might be worth checking one of our American suppliers:
https://www.watlow.com/downloads/en/catalogs/immersion.pdf
You'll have to 'up' your wattage since we're at 480V.
'da Kid
Now that I have a 3-phase outlet in the garage, I am able to connect one of these (a circuit box meant originally for construction sites):
It's got a 16 amp 3-phase input, then 2 x 16 amp 3-phase outputs and 4 x 16 amp 1-phase outputs (2 per circuit). 2 x 16 amp circuit breakers for the 1-phase sockets and a 40 amp RCD (GFCI) for the entire thing.
I can connect a 10 meter 3-phase extension cord to the outlet in the garage and then mount this thing to my brew rig and take it out in the yard! Or use a 3-phase welder, etc.
Do you have such devices in the US? This one only costs 67 EUR.
You can not import electrical devices into the European Union unless they are CE marked. That is roughly the US equivalent of UL marking. They simply won't make it through customs.
http://ec.europa.eu/enterprise/policies/single-market-goods/cemarking/
In addition, every country has it's own organisation that needs to approve all electrical devices being imported or sold in that country. For example, in Germany it's called "TÜV" and in Finland it's called TUKES.
OMG, heck no we don't have anything as gorgeous as that. Here is our closest sad equivalent.
I don't think so, because homes are not wired 3ø in the US (people that want 3ø here have to make it from single phase). Nor do I remember seeing anything like that around shop floors or in labs or office buildings but that prove that they don't exist here.Do you have such devices in the US?
I don't thing so, because homes are not wired 3ø in the US (people that want 3ø here have to make it from single phase). Nor do I remember seeing anything like that around shop floors or in labs or office buildings but that prove that they don't exist here.
Curious as to why only two of the phases are supplied to single phase outlets. Are you fed corner delta?
What I am a bit jealous of is your 3ø power. I could do so much more at home if i had that.
A quick note. This is what I'm used to for quick power distribution on job sites in the US.
I remember asking an engineering professor that same question. I.E. If a three phase motor is more efficient than single phase, how huch more efficient is it? He said without hesitation, "20 percent". I don't know if that is true, and that was in 1980, so things may have changed somewhat since then. However, you still can't get something for nothing. Compare full load amps on each machine. That's where the HP calculation comes from, so they can't be too far away from each other. One way of looking at the whole question would be to approach it form the "green" point of view and consider how much copper and iron are going to produce the same effect. As Tony says, "Looks can be deceiving". Generally, the 1 ph motor will have twice as much copper and iron as the 3 ph motor. That extra stuff is devoted exclusively to starting the 1 ph motor. When it gets up to normal operating speed, the centrifugal switch takes it out of the circuit. And as said earlier, the 3 ph motor runs cooler. I would attribute some of that to the start function in the 1 ph motor. WWQ
Are you saying that compressor motors in home heat pumps, for example, would be single phase?
Not to say that you don't have your own limitations with what you have.