need to plug into a 20 amp receptacle, like on a kitchen counter. two of them will not work.
Oups. I don't know if I have one.
Does a standard outlet will work too?
Oups. I don't know if I have one.
Does a standard outlet will work too?
Goto home depot or your frenchie equivilent and install one yourself? Only like $10 bucks for a 20A GFCI Breaker i think
Oups. I don't know if I have one.
Does a standard outlet will work too?
Code generally states that the 100% "on" load be 20% less than the rated max..Fred
however ... if the outlet you are plugging into is really close to the panel -- like 15'-20' away and not much more, and you're house was built in the last 30yrs or so, you'd actually be fine. Maybe (probably) violating local code, but fine.
What about using one of these if I have the proper amperage but no GFCI plug?
http://www.homedepot.com/p/Defiant-Plug-In-GFCI-Adapter-3-Wire-Grounding-30339036/203741464
Nothing wrong with using those for your GFCI protection assuming proper amperage.
This is pretty bad advice...14 AWG is rated for 15 amps...regardless of distance to panel. He will still be drawing more then 15 amps. As I said in a different thread there is a reason why code is the way it is and why they limit 14 AWG to 15 amps. Being fine does NOT mean you are being safe.
Arrrrr.. I got a headache
Again if he tests the element he will find it draws less the 15 amps at 100% power.. I would bet money on it.
whether it draws 15 amps or less is irrelevant from a code standpoint. not saying there is an inherent danger by running this on a 15 amp circuit if it in fact draws less than 15 amps but from a code-standpoint, it is a violation.
Again if he tests the element he will find it draws less the 15 amps at 100% power.. I would bet money on it.
Its a homemade non CE or UL listed appliance... Whether it does or doesnt technically meet code wont matter here. they have an easy out to not pay the claim.
I agree that the arguments will never end. But, it's bad engineering practice to eliminate the safety margins designed in place. That's not refutable.
-BD
ok but you are missing the point that the elements are not correctly rated at the right power to begin with... Every element vary's a bit in actual power output. because they are manufactured for like $2 a piece they just use a foolproof system of rounding up the power output to the closest standard advertised size. To save money they test then as long as they come remotely close but still fall under the rating they are labeled as such...I agree with what you are saying from a math stand point. Regardless, code is there for a reason and it's still a code violation. When dealing with electricity it's always better to be on the safe side it's not worth risking injury or a fire for a few extra watts.
Its not only just about insurance. It's about staying safe and minimalizing the risk to yourself.
ok but you are missing the point that the elemnts are not correctly rated at the right power to begin with... to save money they test then as long as they come remotely close but still fall under the rating they are labeled as such...
Its not unusual for a 1500w element to actually put out 1200w for example.
THINS is why a smart engineer would check the element and build accordingly... You are still allowed to think for yourself you know. if the element draws 13.5 amps it would be foolish to rewire your house just to meet a code which relates to an element that draws 15.86amps or whatever when thats not really what you have.
THIS is why a smart engineer would check the element and build accordingly... You are still allowed to think for yourself you know. If the element draws 13.5 amps it would be foolish to rewire your house just to meet a code which relates to an element that draws 15.86amps or whatever when thats not really what you have. You would STILL meet code if your element is actually closer to an 1800w element and draws under 15 amps which I am fairly certian it will be.
I believe this is also an old argument...except when code says you can't.
210.23(A)(1) explicitly states that 'the rating of any one cord-and-plug-connected utilization equipment not fastened in place shall not exceed 80 percent of the branch-circuit ampere rating'. so a 15 amp circuit would limit you to a load that draws 12 amps, regardless of its nameplate rating or whether it is continuous or not.
again, not necessarily a dangerous situation but absolutely a code violation. the code is full of a lot of stuff that doesn't make practical sense but it is what it is. for example, emt needs to be secured within 36" of a box. if it is fastened at 37" is it a dangerous situation? of course not but it is still a violation. but then again, driving 56 in a 55 zone is also a violation.:cross:
personally, i would plug it in and see if it works.
I believe this is also an old argument...
That 80% code only applies to instances where the max load is being drawn in continuous operation for more than 3 hrs. not for a plug in appliance that only draws for an hr or so.
i can't speak to arguments before i joined this forum but since the load in question in this thread is plugged into a convenience receptacle, the code section i referenced is totally applicable. there is not a distinction made between continuous and non-continuous for plug-connected utilization equipment. if this device was hard-wired, the referenced code would not apply. not a dangerous situation but a code violation nonetheless.
and i totally agree this is a non-continuous load, as defined by the nec. even a pid controlled element boiling for ten hours wouldn't qualify, as it turns off and on. as silly as it sounds, a load operated for 2 hours, 59 minutes and 59 seconds which is turned off for just one second no longer qualifies as a continuous load. the 'absolutes' in the code can be used to an advantage on occasion.
and totally agreed on the op, they can do whatever they want. my biggest 'beef' with all this is disingenuous statements like 'it isn't a code violation' or 'it works so what's the problem' and the like (not saying you said that). folks should at least have the background information and make their own decisions. i have several minor code violations in my house but the distinction is i know they are violations. i've assessed the situation and made what i feel to be an educated decision. someone making a decision based on some guy on the internet saying 'bah, it's cool dude' is bad mojo.
just my $0.02...