Just took apart the AC...that was easy... now bending the tubing without creating a paper weight... any tips? go very slowly and carefully... yeah..

what about orientation? does it have to sit the same way basically for it to work properly? i have seen some tilted down or sideways... just curious...

I plan on using my BCS 460 to control ferm temp in the Blichmann 14 gal with a new cooling coil i just discovered on the way!
 

Attachments

  • Photos.zip
    1.2 MB · Views: 87
20180820_171421.jpg
 
You must maintain the original orientation of the compressor as it has a lubricant sump at its original "bottom" end.
Otherwise you can go as nuts as the tubing will allow (which likely isn't much)...

Cheers!
 
You must maintain the original orientation of the compressor as it has a lubricant sump at its original "bottom" end.
Otherwise you can go as nuts as the tubing will allow (which likely isn't much)...

Cheers!
Ok I just meant the evap coil...not the whole unit...

Just rough test now...
 
Not ideal but just testing...pulled it right down to 36 before I stopped...4 gal plain water..
 
Right. And what I meant was you have to keep the compressor in its original orientation, but anything else you can move as much as your luck allows...

Cheers!
So what is the ideal temp to keep the chiller water at? freezing might be too cold... but im not sure... was thinking low 30s.
 
With mine, I found that with a 50/50 propylene glycol mix, I could get the solution down to about 23℉ or so before it got difficult to pump. I also learned that propylene glycol is hygroscopic. Rather than evaporating, my reservoir filled itself up. It also diluted the solution, gradually decreasing the effectiveness. This has been over about three months or so of South Florida heat and humidity. I've also read that most industrial/commercial glycol systems are closed loop, but I'm not sure how to accomplish that in my rig.
 
With mine, I found that with a 50/50 propylene glycol mix, I could get the solution down to about 23℉ or so before it got difficult to pump. I also learned that propylene glycol is hygroscopic. Rather than evaporating, my reservoir filled itself up. It also diluted the solution, gradually decreasing the effectiveness. This has been over about three months or so of South Florida heat and humidity. I've also read that most industrial/commercial glycol systems are closed loop, but I'm not sure how to accomplish that in my rig.
Ok thats good info, i am in Georgia, but downstairs is AC'd... so humidity isnt a problem but thanks for that info...

is 23 too cold? for the conical? its 14 gal conical so maybe not... what kind of pump are you using to circulate with? I wouldnt think you would want too high a flow rate...
 
I built a 54w x 33d x 30h ferm chamber, and built a heat exchanger out of a transmission cooler I bought from Amazon and two 4" muffin fans. I submerged a backyard fountain pump in the reservoir that pumps the solution through the hx. I have some pics at this thread for reference.
 
So what is the ideal temp to keep the chiller water at? freezing might be too cold... but im not sure... was thinking low 30s.
I dont go lower than 28 degrees myself to avoid ice (on condenser/coils but I only use like 30% glycol since I read that water actually cools better and like a car too much antifreeze doesnt cool as effectively. ive had my system going for over 3 years and occasionally top off the water and had to add glycol once when I had a cooling coil burst (I was experimenting with surgical tubing around a fermenter which could not stand up to colder temps) .. other than that its been working flawlessly using one pump and 4 soleniod valves to cool 4 fermenters.
 
I dont go lower than 28 degrees myself to avoid ice (on condenser/coils but I only use like 30% glycol since I read that water actually cools better and like a car too much antifreeze doesnt cool as effectively. ive had my system going for over 3 years and occasionally top off the water and had to add glycol once when I had a cooling coil burst (I was experimenting with surgical tubing around a fermenter which could not stand up to colder temps) .. other than that its been working flawlessly using one pump and 4 soleniod valves to cool 4 fermenters.
I only have the one conical now, so i will just use the BCS to control an Aq pump to pump to the conical.... i might pick up one later on, but they are a bit pricey...
 
especially the blichmann conicals...
i bought it used and paid 350 for it which i though was a good deal... and its nice and all... but i see they came out with a SS coil that will go inside it... not sure what other kind of conical i would get though... hard to justify that much money for more than one...esp when i already have a free fridge i use for my kegs
 
I got it pretty much bent where i need it now. I am just waiting on the temp probes from Brewers Hardware to connect to my 460... taking forever!!

what do you guys recommend to use for hoses? vinyl? Silicone? thought about using PEX tubing and insulate it...

I was reading up on the E Brewery site and he is using RV antifreeze and not glycol... anyone else do this?
 
Vinyl works fine, but it does get stiff when it gets that cold. It's what I use just because it was cheap. Silicone is better if you want to spring for it. PEX works well if you're hard plumbing.

Lots of people use RV antifreeze. Since it never comes in direct contact withy our beer, it should be fine in theory. Personally I pay the extra money for the food-grade glycol just for my peace of mind.
 
For those of you building these, how did you determine what size a/c unit to buy? I currently have a half barrel Spike conical and expect to add another one within the next year.
 
In my case I just used the 5k BTU unit I had lying around... im still building however as Brewers Hardware has STILL not sent the temp probe...
 
Thanks. My friend used a 5K, but his conical only holds 8 gallons. I've been trying to find a 10 - 12K, but want to stay under $150 and not having any luck. May just go with 8K for now and see how that works. I am going with a cooler thst holds at least 12 gallons so that should help when I add another fermenter.
 
I will be doing appx 11 gal in the fermentor... hoping I can get it to 50... when i did a test run i got at 33 before i stopped , just in the chiller tank itself, so it should be cold enough. I guess it also depends on where it is... mine is in basement which itself is 70 degrees year round... if you were in a warmer environment i would imagine it would take more...
i see a lot of AC units on sale at HD and Lowes this time of year you could probably pick one up cheap enough...

If BH ever decides to send the temp prob i can hook it all together...
 
I got the rest of the stuff, the other probe and thermowell... after couple weeks... BO was stamped on it, my issue is that 4 emails and not a single reply telling me next week month or year or ever!

soo broke down and called... seems they are out of the 4 in, for several weeks.. but they had longer ones... i said size wasnt the issue so he is sending a 6in out today... depending upon when i get it will see how it does...
 
Last edited:
I dont go lower than 28 degrees myself to avoid ice (on condenser/coils but I only use like 30% glycol since I read that water actually cools better and like a car too much antifreeze doesnt cool as effectively.
True but when we do heat transfer calculations with water we multiply gpm by 500 (=60 min/hr*8.34 pounds/gal*BTU/lb•°F) to get the heat transfer in BTU/hr per °F temperature difference. For glycol mixtures of typical strength (50%) we drop that to 485 i.e. by only 3%.
 
True but when we do heat transfer calculations with water we multiply gpm by 500 (=60 min/hr*8.34 pounds/gal*BTU/lb•°F) to get the heat transfer in BTU/hr per °F temperature difference. For glycol mixtures of typical strength (50%) we drop that to 485 i.e. by only 3%.
your likely right but 30% has been working fine for me for a few years now without the mixture freezing up or getting nasty so...
if you go even as low as 28 degrees it promotes freezing of ice around the outside of the cooling coils for the fermenters with the coils inside which is why places like spike recommend 30 degrees..
 
what about orientation? does it have to sit the same way basically for it to work properly? i have seen some tilted down or sideways... just curious...

It's been noted already that the compressor sump must be down for lubrication. Common sense says you'd want the discharge from the compressor to go into the top of the condenser so as to form a pool of liquid at the bottom of it to separate high from low side which, as the picture shows, you have here. But common sense also says you would want the capillary to spray into the top of the evaporator so that the droplets will fall under gravity thus using as much of its surface for absorbing heat as possible. But that's exactly the opposite of this design. Conclusion: my common sense isn't that sensible and it doesn't matter what position the evaporator is set in. It should, for best efficiency, of course, be completely in the water bath.
 
ok got it mostly hooked up... however for whatever reason the compressor is not running? it was when i tested it... but not now...is there a way to test to see if its getting power? there are 3 wires... Red Black Blue...

also when BCS shuts off... the AC wont come back on when told to, i have to turn it on... somehow i have to bypass digital controller?
 
Black is probably the common, red is probably the run winding and blue probably the start winding but those are just guesses. Look for markings on the side of the compressor body like R,S,C to verify. The first thing to do is disconnect those wires preferably not at the compressor end and noting which wire was connected where so you can put it back and measure between them with an ohm meter. Between C and R you should measure a few ohms. Between C and S you should measure a few more. If either of these measurements gives you 0 or open then the compressor is shot and needs to be replaced. The next thing to do is to figure out how the compressor is started. There will be a capacitor or capacitors involved which in the pictures you have posted appear to be integral to the compressor itself i.e. inside the hermetic can. That, I would think, would not be something that the manufacturer would do as capacitor failure is pretty common (just happened on my heat pump - as soon as the weather turned cool and we turned it on) and is an easy fix - if you can access the caps. But perhaps on these $130 units it is cheaper to throw them away and buy a new one as I can't imagine getting a repairman to your house and having him fix something for less than $130. If you can access the capacitors use your multimeter to check that their capacitances are approximately as labeled. If the cap(s) check out then turn your attention to the control part of the circuit. There are several ways to start a compressor involving various types of relays (or not) so I can't comment on what you may actually have. In small, cheap units it's common to just have a run capacitor connected all the time between the R and S windings. In more sophisticated designs there may be a separate relay, a "start assist kit" may be installed or there may be a controller circuit board which manages the S winding connection. You will have to trace the wiring through from the black (hot wire) in the line cord through to the compressor. In a normal start cycle voltages, but not necessarily the same voltage, will appear immediately on both the start and run windings. After a second or two the voltage on the start winding may change but the run winding voltage should stay at close to line voltage (120). If you are lucky a wiring diagram will be attached to the inside of the cabinet somewhere. If there is one take a pic of it. This will make it much easier to give you better directed suggestions.

Don't know what a BCS is so can't comment on that.

One more thing: check for a thermal overload switch on the compressor body and make sure it is, if tripped, reset.
 
Black is probably the common, red is probably the run winding and blue probably the start winding but those are just guesses. Look for markings on the side of the compressor body like R,S,C to verify. The first thing to do is disconnect those wires preferably not at the compressor end and noting which wire was connected where so you can put it back and measure between them with an ohm meter. Between C and R you should measure a few ohms. Between C and S you should measure a few more. If either of these measurements gives you 0 or open then the compressor is shot and needs to be replaced. The next thing to do is to figure out how the compressor is started. There will be a capacitor or capacitors involved which in the pictures you have posted appear to be integral to the compressor itself i.e. inside the hermetic can. That, I would think, would not be something that the manufacturer would do as capacitor failure is pretty common (just happened on my heat pump - as soon as the weather turned cool and we turned it on) and is an easy fix - if you can access the caps. But perhaps on these $130 units it is cheaper to throw them away and buy a new one as I can't imagine getting a repairman to your house and having him fix something for less than $130. If you can access the capacitors use your multimeter to check that their capacitances are approximately as labeled. If the cap(s) check out then turn your attention to the control part of the circuit. There are several ways to start a compressor involving various types of relays (or not) so I can't comment on what you may actually have. In small, cheap units it's common to just have a run capacitor connected all the time between the R and S windings. In more sophisticated designs there may be a separate relay, a "start assist kit" may be installed or there may be a controller circuit board which manages the S winding connection. You will have to trace the wiring through from the black (hot wire) in the line cord through to the compressor. In a normal start cycle voltages, but not necessarily the same voltage, will appear immediately on both the start and run windings. After a second or two the voltage on the start winding may change but the run winding voltage should stay at close to line voltage (120). If you are lucky a wiring diagram will be attached to the inside of the cabinet somewhere. If there is one take a pic of it. This will make it much easier to give you better directed suggestions.

Don't know what a BCS is so can't comment on that.

One more thing: check for a thermal overload switch on the compressor body and make sure it is, if tripped, reset.
 

Attachments

  • comps3.jpg
    comps3.jpg
    747.7 KB · Views: 90
  • comps2.jpg
    comps2.jpg
    1 MB · Views: 85
  • comps1.jpg
    comps1.jpg
    847 KB · Views: 94
Those help a whole lot. The way this is wired when the 'controller' decides that it wants cooling it energizes the blue wire. Thus the high level test involves taking off the blue wire, attaching a voltmeter between the pin you took it from (on the board) and neutral (or ground) and adjusting the controller (temperature set point) to a value well lower than the room temperature. Before disconnecting the blue wire find the overload and make sure it is closed (reads 0 ohms across its terminals).

Lowering the thermostat setting should cause the thermostat to close and the controller to put voltage on the blade to which the blue wire connects. If this does not happen then the controller or transformer is defective. About all you can do from there is check the transformer.

If the controller does put voltage on the blue wire pin then it is working properly and you can proceed to check the cap. There are two sections: 5 and 25 uFd. Remove the wires from the cap before testing it but be sure to make notes or take pictures to allow you to get the wires back onto the right terminals. This is critical. If the cap passes then move on to check the compressor winding resistances. Check between the ends (at the capacitor) between the blue wire and the black wire and between the blue wire and the red wire. You should get a reading of a few ohms for each. The blue/red reading should be higher than the blue/black reading. A reading of OL or infinity for both would suggest the overload is open in which case you should double check that.
 
Thank you so much!! Sorry my bd today so didnt get to it...so does C mean compressor? Will do this tomorrow when I get home...
I will mention one of the black wires on cap came off...not sure exactly which spot it goes back in...there are two terminals that it can go...it goes to a black round thing up top...thermostat?


Those help a whole lot. The way this is wired when the 'controller' decides that it wants cooling it energizes the blue wire. Thus the high level test involves taking off the blue wire, attaching a voltmeter between the pin you took it from (on the board) and neutral (or ground) and adjusting the controller (temperature set point) to a value well lower than the room temperature. Before disconnecting the blue wire find the overload and make sure it is closed (reads 0 ohms across its terminals).

Lowering the thermostat setting should cause the thermostat to close and the controller to put voltage on the blade to which the blue wire connects. If this does not happen then the controller or transformer is defective. About all you can do from there is check the transformer.

If the controller does put voltage on the blue wire pin then it is working properly and you can proceed to check the cap. There are two sections: 5 and 25 uFd. Remove the wires from the cap before testing it but be sure to make notes or take pictures to allow you to get the wires back onto the right terminals. This is critical. If the cap passes then move on to check the compressor winding resistances. Check between the ends (at the capacitor) between the blue wire and the black wire and between the blue wire and the red wire. You should get a reading of a few ohms for each. The blue/red reading should be higher than the blue/black reading. A reading of OL or infinity for both would suggest the overload is open in which case you should double check that.
 
Well happy birthday!

'C' stands for "Common". Both the compressor and capacitor have terminals marked this way. In the compressor the two windings (S - start and R - run) are connected together at one end and that connection goes to the common terminal. The free ends go to, respectively, the R and S terminals. In the capacitor can one terminal from each of the two individual capacitors in the can are connected together and to the common terminal. The other sides of the capacitors go to, respectively, the FAN and HERM terminals.

There are, apparently, three black wires going to the capacitor. Two are from a start assist which appears to be under the transformer in the photo. The two wires from that go to the capacitor C terminal and the other to the capacitor HERM terminal. The third black wire comes from the R (run) winding on the compressor. It also connects to the C terminal on the capacitor. This is the one that goes to the "black round thing up top" which I am assuming is the thing to which the red, black and blue wires all run together, the thing with S, C and R molded into the top, the left of two cylinders on top of the compressor. That's not the thermostat. That's where the wires enter the compressor through a glass hermetic seal.

In summary, there are 3 terminals on the capacitor. One is labeled "FAN" and should have a single wire of color "TM", whatever that means - it appears to be yellow in the photo. The second is labeled "C" and should have a white wire running from it to the fan motor, a black wire running to the R terminal on top of the compressor and another black wire running to the circuit board start assist. The third terminal is labeled "HERM" and should have a single red wire running from it to the S terminal on the top of the compressor.
 
Thank you SO MUCH for all this...
I did want to say the loose wire I found goes to the black round thing in the wiring pic... at the left hand side, there are two of them and they both go to the Cap...I "think" i put it back but am not sure... will look more in detail this afternoon and do some troubleshooting...

again thank you so much for all this!!

Well happy birthday!

'C' stands for "Common". Both the compressor and capacitor have terminals marked this way. In the compressor the two windings (S - start and R - run) are connected together at one end and that connection goes to the common terminal. The free ends go to, respectively, the R and S terminals. In the capacitor can one terminal from each of the two individual capacitors in the can are connected together and to the common terminal. The other sides of the capacitors go to, respectively, the FAN and HERM terminals.

There are, apparently, three black wires going to the capacitor. Two are from a start assist which appears to be under the transformer in the photo. The two wires from that go to the capacitor C terminal and the other to the capacitor HERM terminal. The third black wire comes from the R (run) winding on the compressor. It also connects to the C terminal on the capacitor. This is the one that goes to the "black round thing up top" which I am assuming is the thing to which the red, black and blue wires all run together, the thing with S, C and R molded into the top, the left of two cylinders on top of the compressor. That's not the thermostat. That's where the wires enter the compressor through a glass hermetic seal.

In summary, there are 3 terminals on the capacitor. One is labeled "FAN" and should have a single wire of color "TM", whatever that means - it appears to be yellow in the photo. The second is labeled "C" and should have a white wire running from it to the fan motor, a black wire running to the R terminal on top of the compressor and another black wire running to the circuit board start assist. The third terminal is labeled "HERM" and should have a single red wire running from it to the S terminal on the top of the compressor.
 
OK so Blue wire is hot, check.
Blue red is 5 ohms blue black is 1.8 ohms
Cap i have not checked yet... there are 3 terminals on it... which ones do i test with my fluke?

ok one side was 4.9 micro F and the other was open... so i guess thats the bad part.... ?

Those help a whole lot. The way this is wired when the 'controller' decides that it wants cooling it energizes the blue wire. Thus the high level test involves taking off the blue wire, attaching a voltmeter between the pin you took it from (on the board) and neutral (or ground) and adjusting the controller (temperature set point) to a value well lower than the room temperature. Before disconnecting the blue wire find the overload and make sure it is closed (reads 0 ohms across its terminals).

Lowering the thermostat setting should cause the thermostat to close and the controller to put voltage on the blade to which the blue wire connects. If this does not happen then the controller or transformer is defective. About all you can do from there is check the transformer.

If the controller does put voltage on the blue wire pin then it is working properly and you can proceed to check the cap. There are two sections: 5 and 25 uFd. Remove the wires from the cap before testing it but be sure to make notes or take pictures to allow you to get the wires back onto the right terminals. This is critical. If the cap passes then move on to check the compressor winding resistances. Check between the ends (at the capacitor) between the blue wire and the black wire and between the blue wire and the red wire. You should get a reading of a few ohms for each. The blue/red reading should be higher than the blue/black reading. A reading of OL or infinity for both would suggest the overload is open in which case you should double check that.
 
Last edited:
Yes, you should measure close to 5 uFd between pins C and Fan and close to 25 between pins C and HERM. If you measure open between C and HERM the cap is bad. There is only one thing that bothers me a little here. Is this not a fairly new unit? A cap should last about 5 years. I just had one fail on my heat pump but it has been here st least as long as I have (about 5 years).

Yes, that's the right size cap and I can vouch for the brand. I just installed one of those and it has run for 3 whole hours so we know they last at least that long.

And the compressor winding resistances look good.
 
Yes I barely used it...but it has sat for a few years unused...
When I ran my test it maybe ran 30 min then I stopped once bath got down to 35 or so about a month ago...
Then I built platform and put it and cooler in it and plugged it in...and didnt work...it looks perfectly fine but I guess being open on comp side not..


Yes, you should measure close to 5 uFd between pins C and Fan and close to 25 between pins C and HERM. If you measure open between C and HERM the cap is bad. There is only one thing that bothers me a little here. Is this not a fairly new unit? A cap should last about 5 years. I just had one fail on my heat pump but it has been here st least as long as I have (about 5 years).

Yes, that's the right size cap and I can vouch for the brand. I just installed one of those and it has run for 3 whole hours so we know they last at least that long.

And the compressor winding resistances look good.
 
In all this i forgot the most important question... is there a way to bypass the E control? the BCS is just a basic controller, turning on and off the power to the AC unit itself... like plugging and unplugging it from wall... every time i power it up it goes back to basic idle state... is there a way to bypass this>? if not i may have to not worry about the cap...to keep the temp in the bath a constant temp like 30 degrees etc...

Yes, you should measure close to 5 uFd between pins C and Fan and close to 25 between pins C and HERM. If you measure open between C and HERM the cap is bad. There is only one thing that bothers me a little here. Is this not a fairly new unit? A cap should last about 5 years. I just had one fail on my heat pump but it has been here st least as long as I have (about 5 years).

Yes, that's the right size cap and I can vouch for the brand. I just installed one of those and it has run for 3 whole hours so we know they last at least that long.

And the compressor winding resistances look good.
 
All you have to do to make the compressor run is disconnect the blue wire from the circuit board and apply 120 VAC to it. This should be through a relay rated for the compressor load current which relay is operated by the BCS. If the BCS has internal relays that can handle the compressor load the extra relay isn't necessary. Doing thus takes the A/C unit's internal thermostat out of the picture.

You will still need the 25 uFd capacitor. That's what spins the magnetic field inside the compressor motor. Without it the compressor will not run. Just hum and get hot.
 