Has anyone ACTUALLY used a chest freezer as a glycol chiller

Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum

Help Support Homebrew Talk - Beer, Wine, Mead, & Cider Brewing Discussion Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

radial67

Active Member
Joined
Oct 14, 2011
Messages
43
Reaction score
0
Location
Australia
So Ive been reading through a number of threads and there is a real healthy and constructive Aircon/chest freezer rivalry going on and I was interested whether anyone has actually used a Chest Freezer as their glycol chiller or whether it always comes back to how little BTU's they actually have.

Im starting up a 2bbl brewery and dont want to have to fork out a ton of money for a proper glycol chiller as its a single point of failure and super expensive for a chiller capable of running 8 zones+cost of plumbing, whereas chest freezers are cheap, readily available and one per fermenter reduces the single point of failure.

I cant do aircons because of increased ambient temps caused by the fans will interfere with the already increased ambient temps (tropics) and a limitation of free airspace ventilation.

So - has anyone actually successfully done a chest freezer glycol chiller?
 
There have been at least a few I've seen written up in the forums. Here is one example thread that appears to have been a success, with a pretty good size fermenter - and located in New Mexico, USA.

At least one key is to actually fill the freezer with the working fluid - be it glycol or brine - so the coils are doing the cooling directly without air working against the thermal transfer (ie: a bucket in a chest freezer is not going to work very well if at all). Another is finding a pump that doesn't put too much heat into the efficiency equation..

Cheers!
 
Wasnt thinking of using coils.... its just another way of losing temp. I was going to pump chilled Poly-glycolUSP directly through the jackets on the fermenters.

Pump would be on the return side of the fermenter so as not to warm up the glycol gg to the fermenter.
 
fwiw, the "coils" I was referring to are the cold side coils buried in the freezer walls, not whatever you would use around/in the fermenter at the other end of the loop. They're usually mounted high up in the chest freezer walls, so the working fluid level would want to be pretty high up as well to maximize thermal transfer...

Cheers!
 
Hold on there tiger. Let's get this straight--no matter which you use, be it an air conditioner or a chest freezer, the same amount of heat is going to need to be removed from the fermenter. There might be slight differences in the efficiency of the airconditioner vs the chest freezer, and the air conditioner is going to have a MUCH higher output capacity (and therefore lower duty cycle) than a chest freezer, but at the end of the day you need to move X amount of Joules over Y amount of time.

Chest freezers tend to have relatively small compressors. This is due to the inherently efficient design--only allowing the top to open keeps a vast majority of the cool air in. As a result, if you're going to be cooling a lot of 2BBL fermenters, I have a hard time suspecting that a chest freezer is going to be sufficiently powerful for the occasion.

A modified air conditioner with the evaporator coils dunked in a coolant reservoir is going to have a LOT more cooling capacity than a chest freezer could. This was, at least at one time, a fairly common way of performing sub-zero CPU cooling for computer overclocking...An older hobby of mine :D.

I am an electrical engineer also certified as an HVAC tech :p. I'll try to answer any questions you may have :).
 
Everyone’s comments bring up valid reasons to use one method over another. I am working on putting the finishing touches on my 15 gallon system with a 16 gallon induction tank (plastic conical) and my plan is to use my beer cooler for the chiller. Considering that the fermentation unit will only hold 15 gallons I plan on making an insulated jacket with tubing on the inside for cooling and have it go into my restaurant beer cooling with a five gallon bucket of brine for chilling. I will have a PID controller running the pump and hopefully keeping it in the desired range. The nice thing about the two keg beer cooler is that can bring things to temperature very quick. It only took two hours to bring my 7.5 gallon keg to 40 degrees so I don’t think I will have any issues with the other.

The new deep sink is installed and the fermenter stand is off being powder coated so all that is left to do is run the 50 amp circuit for my RIMS unit and install the arduino controller, from there I just have to wait for the stand to come back so I can test

Below is the new 15 gallon RIMS unit I built; currently it has a 4500 watt and 1500 watt heater and a March 809 pump. After I run a couple tests I will finalize my design and build a new stand and change from silicone tubing to rigid lines.

rims_pre_test.jpg
 
Ok, some background - I've built glycol chillers for three are micro-brewery's now (ranging in size from 1.5 bbl to 3 bbl) so I've got a little experience in the area.

The biggest problem you'll run into with a chest freezer is the size of the cooling system. Most of them are going to fall somewhere between 500 and 1500 btu/hr. 3 bbl of very active yeast (such as one that would drop 40 pts in 24 hrs) will put out in the neighborhood of 500 btu/hr. Now granted this isn't normal, but does give you an upper bound for the heat put out by yeast. Add into that heat loss's to the surroundings (assuming times when the room is warmer than the desired ferm temp) and you can quickly overwhelm a chest freezer.

You can offset some of these effects by having a larger resevoir of glycol, and has been mentioned above, you would almost have to to have any sort of performance from the chest freezer. Basically fill it up almost directly, without using a bucket, so you have conduction to the cooling coils to transfer the heat out. If you just put a bucket in, you'll get even slower performance because air is an insulator.

What I've done several times now is take a standard 8-12,000 btu/hr window aircon unit, seperate the evaporator out but cutting part of the frame away, and submersing that into a rectangular cooler. You lose about 20% efficiency from the aircon because you're operating it at lower than design temps, but it's still more than adequate and with the added capacity, you can crash cool effectively.

I have a 10,000 btu/hr unit at a brewery that is running 11 - 3 bbl fermentors with this setup, and is coming up on 2 years of continuous use. they are able to crash cool, and even lager some beers without much trouble.

If you have questions on the setup, feel free to ask. For converting an Aircon, I can't give specific instructions because they're all a bit different, but I can say I've been able to do it for under $500 each time for the glycol chiller portion.
 
As for the single point failure aspect - you can always back it up with a trash can filled with ice in a pinch
 
Shockerenger--Exactly what I was suggesting with the air conditioner :).
 
This thread may be dead but I'll give it a shot.

I've been using a 5K window aircon for the past 1.5 years for our 3 little 15 gallon plastic conicals with coils. It works great for regular ale temps. When I try to get the glycol down below 25F, the insides of the aircon get totally ice packed and it won't go any lower.

Should I be able to get down lower? I'd like to see 15F.

One other thing. I'm using a ~40 qt cooler with 8 gallons of the good glycol, but, the pump is also in the cooler. Wondering if the pump might be the limiting factor. It's a .5Hp sump pump.
 
This thread may be dead but I'll give it a shot.

I've been using a 5K window aircon for the past 1.5 years for our 3 little 15 gallon plastic conicals with coils. It works great for regular ale temps. When I try to get the glycol down below 25F, the insides of the aircon get totally ice packed and it won't go any lower.

Should I be able to get down lower? I'd like to see 15F.

One other thing. I'm using a ~40 qt cooler with 8 gallons of the good glycol, but, the pump is also in the cooler. Wondering if the pump might be the limiting factor. It's a .5Hp sump pump.
 
If it's freezing up, then there isn't enough glycol:water. The coils will run about 15F below what the glycol is, unless it's freezing up, in which case it can drop even further.

A small pump recirculating can actually help by keeping the water moving, but it has limits.

You specify "The good glycol" but not exactly sure what is meant by that.

15F is probably beyond what is reasonably achieved with a window unit, even with sufficiently low freezing point of the glycol. The overall system efficiency of most window units really starts to dive off once you go below 25-30F, meaning your effective capacity is much lower at those temps, which is probably counter productive to what you are trying to do.

Again, not knowing the rest of your setup, but insulation of the conical's is probably a better bet to achieve your goals.
 
Thanks for the response Shockerengr.

It isn't the coil inside the cooler that's freezing up. The components outside of the cooler in the AC itself are all covered with ice. I think the parts are the compressor and expansion valve. My return water to the cooler is set up so that it runs over the coil in the cooler and it's adequately covered so that never really freezes.

I was initially using RV type antifreeze at about $4/gallon. Switched to using CrytoTek at about $20/gallon with dilution for around -30F or so.

I've got the conicals wrapped in foil faced bubble and the tubing in neoprene.
 
Thanks for the response Shockerengr.

It isn't the coil inside the cooler that's freezing up. The components outside of the cooler in the AC itself are all covered with ice. I think the parts are the compressor and expansion valve. My return water to the cooler is set up so that it runs over the coil in the cooler and it's adequately covered so that never really freezes.

I was initially using RV type antifreeze at about $4/gallon. Switched to using CrytoTek at about $20/gallon with dilution for around -30F or so.

I've got the conicals wrapped in foil faced bubble and the tubing in neoprene.

I'm curious to see the experts way in on this. I'm deconstructing a window AC this weekend, and I want to maker sure I understand everything first.

As to the OP's original question, there is no way a chest freezer has enough power. A HUGE chest freezer might not have over 1000 BTUs, but the smallest window AC packs about 5000.

I have a SSBrewtech conical with the stainless coil for chilling. I know it wouldn't work well, but I wanted to test it with a water reservoir in a smallish mini-fridge. I could get the temps about 10 degs below ambient, but no more than that. The lines and conical were insulated.
 
Ah, gotcha, that's not unusual then, just means the unit is running a lot. It's condensation freezing on all the exposed low temps parts, so anything from the orifice or expansion valve all the way back to the compressor itself, and possibly the compressor housing if you're running cold enough. If the evaporator coil is still clear, then the unit is still functioning.

The reason you can't get much colder has to do with the physics of the design of the system. Most are using R-134a (although not all) and the pressures on the cold side get really low. At 25F glycol, the gas side pressure is probably hovering around 1-2 psi, vs a more typical 20-30psi in normal temp ranges. Just isn't much there to transfer heat.

Anecdotely (haven't measured it) but below 30F, I seem to have about 1/4 of the cooling power, about 10% below 25F.
 
So even if I went to a higher BTU AC, it's probably not going make it any better since we're trying to push these things outside of the specs they were designed for. That all makes sense. My system can get my 15 gallon conicals (3 of them) down to about 34F which is good enough.

Thank you for the clear explanation.
 